Tier III on the wall vs Tier III in reality

Datacenter Talk by FlowSana 24 replies 1.8K views
#11

Has anyone actually verified a certificate with Uptime Institute directly? I tried once, the provider gave me a cert number, UI said "that certificate expired in 2021." Provider claimed "renewal is in process." That was 18 months ago.

#12
Rob34 said:
UI said "that certificate expired in 2021"

You can check certificate numbers at uptimeinstitute.com/tiers. If they won't give you the number, that's the answer. I've had two providers refuse. One said "proprietary." The other said "we're transitioning to a new certification body." Neither is a real thing.

It's always DNS. Always.
#13

Jakarta perspective: most local buyers don't even know Uptime Institute exists. They see "Tier III" on a website and think it's like a hotel star rating. The providers here know this. I've seen "Tier III" slapped on a single-floor office building with one utility feed.

3 #14

Istanbul same. I work with small business clients, they ask me to find "Tier III hosting." I have to explain that without verification it's just a sticker. They don't want to hear it. The sticker is cheaper than real redundancy.

#15

Following this. My current provider claims Tier III, I've never asked for the cert number. Will report back.

#16

Same here.

#17
FlowSana said:
Uptimeinstitute.com/tiers

The Unix philosopher in me wants a whois for datacenter claims. Something machine-readable. Instead we have PDF certificates and sales engineers who disappear after signature.

6 #18

Dubai is full of "Tier III" claims. I visited one facility, they had a beautiful glass-walled server room, no raised floor, and the CRAC units were residential-grade splits from a brand I use in my apartment. The tour guide said "Tier III certified" three times. I left.

#19
HeadRich said:
No raised floor

That's not automatically disqualifying. Aisle containment with overhead cooling is valid. But residential splits, yeah, that's a problem.

#20
astro03 said:
Overhead cooling is valid

Fair. The splits were the problem. Also they had one electrical room, no segregation. I asked about concurrent maintainability and got a blank look.