Skip to content

Mini-guide: reading between lines of 'N+1' claims

Datacenter Talk by steveipw 1 replies 173 views
12 #1

Reading between lines of 'N+1' claims

Three contracts I parsed last month, all said "N+1 redundant":

  • Contract A (Hetzner):
    • One generator, one UPS string
    • "N+1" means spare generator exists... at another facility 40 miles away
    • Switchover: manual, 4-6 hours
    • For that money you get a fuel tank that holds 4 hours
  • Contract B (Vultr):
    • Two UPS modules, one canibus
    • "N+1" means they have a spare module... in a warehouse
    • Install time: next business day
    • For that money you get "electrical diversity" that shares a single utility feed
  • Contract C (OVHcloud):
    • Actual concurrent maintainability
    • But "N+1" only on cooling, not power
    • Generator is N, no +1
    • For that money you get honest labeling at least

I am tired. Post your examples. Goal: crowdsource a checklist.

zfs send | zfs receive. repeat.
#2

Adding two more from RFP season.

  • RackNerd: "N+1" = dual feeds, same substation. We lost both in a planned utility switch. 47 minutes.
  • Leaseweb: "N+1" = two chillers, one pipe. Single point of failure. Maintenance on valve took them offline.
My checklist start:
  • Ask for single-line diagram
  • Ask for maintenance procedure during your tour
  • Ask for last time they tested it
  • Most never test.

436 days. reboot is surrender.