Advice on server closet ventilation in rented apartment
Hot take: my landlord is reasonable but explicitly no modifications. I run three 1U units in a closet, ambient hits 38C in summer. Portable AC unit is allowed, but window venting looks ugly and the hose kit is garbage. For what it's worth, I have a sliding glass door to a small balcony, not a sash window.
Has anyone built custom ducting without drilling holes? I need exhaust path that does not look permanent. Currently running with closet door open and box fan, which is not sustainable. SPF/DKIM for my mail server is finally perfect and I do not want thermal throttling ruining delivery timing.
SPF, DKIM, DMARC — holy trinity ✉️
haroldgsm
Member
Grumpy Old Sysadmin
- Joined:
- May 2024
- Posts:
- 329
- From:
- Ohio, US
I run three 1U units in a closet, ambient hits 38C in summer.
Mark my words, your landlord will notice the condensation trail before they notice a hose.
Dryer vent hose through the sliding door gap, foam board to block the opening. No screws, no damage. I have seen this in twenty apartments. The heat exhausts, the gap seals, you store the board when inspections come. Pessimistic prediction: you will still cook a drive by Christmas.